Quoting my friend skdesigner from a closed thread (Pump Affinity Laws August 2012)
"You don't need to use an affinity law to find pressure at a specific flow."
I agree but then what do you use the affinity laws for?
NFPA 25 8.3.5.2.1:
Theoretical factors for correction to the rated speed shall be applied where determining the compliance of the pump per the test.
and from the handbook:
"NFPA 25 requires the use of affinity laws for correction to the rated pump speed. This correction is needed as the pump ratings were established under ideal factory conditions and most pump performance will vary from the factory ratings under field conditions. Uncorrected pump performance must be sufficient to supply the required system demand as required in 8.3.5.7, to assure that the active systems are properly supported with appropriate pressure and flow."
I'm not understanding the purpose of 8.3.5.2.1 as it applies to a technician doing the test and subsequent report given the last sentence in the paragraph above.
Please correct me if I'm misunderstanding this, but what I read from the handbook is this correction is needed to compare real world test results with perfect world manufacturers test conditions, but it doesn't matter because the real world result are the ones that count.
Regards
D
A thing moderately good is not so good as it ought to be
Thomas Paine
"You don't need to use an affinity law to find pressure at a specific flow."
I agree but then what do you use the affinity laws for?
NFPA 25 8.3.5.2.1:
Theoretical factors for correction to the rated speed shall be applied where determining the compliance of the pump per the test.
and from the handbook:
"NFPA 25 requires the use of affinity laws for correction to the rated pump speed. This correction is needed as the pump ratings were established under ideal factory conditions and most pump performance will vary from the factory ratings under field conditions. Uncorrected pump performance must be sufficient to supply the required system demand as required in 8.3.5.7, to assure that the active systems are properly supported with appropriate pressure and flow."
I'm not understanding the purpose of 8.3.5.2.1 as it applies to a technician doing the test and subsequent report given the last sentence in the paragraph above.
Please correct me if I'm misunderstanding this, but what I read from the handbook is this correction is needed to compare real world test results with perfect world manufacturers test conditions, but it doesn't matter because the real world result are the ones that count.
Regards
D