shacked
Structural
- Aug 6, 2007
- 179
I am the EOR for this custom home that has already been framed and recently the trades; electricians, plumbers and fire sprinkler installers went through to install their wires and pipes. Since the floor joists are 1.75x9.25 microlam lvl joists I have a typical detail for the allowable hole size, spacing and location. Obviously the contractor was not there to supervise the trades since I showed up to the site last week and I see a whole section of joists with 2 large holes located at one end. See the attached picture & sketch of joist span showing holes.
This is a multi million dollar home and I do not believe that the owner should pay for a sub standard performing floor system, therefore I told the contractor that they would have to sister a 2x10 joist to the side of each of these joists, after the wires and pipes were removed. He agreed, but a week later I am now getting push back from the Architect and they do not want to do this.
The floor dead load is 27psf and the calcs for the joist at the reduced sections are still working, but my fear is that the weakened joist floor system may have issues in the long run.
Since it is difficult quantify the performance of the floor system of engineered wood joists with a lot of holes drilled through their length, I think that my fix is reasonable considering the cost of the home. What are some of your thoughts?
This is a multi million dollar home and I do not believe that the owner should pay for a sub standard performing floor system, therefore I told the contractor that they would have to sister a 2x10 joist to the side of each of these joists, after the wires and pipes were removed. He agreed, but a week later I am now getting push back from the Architect and they do not want to do this.
The floor dead load is 27psf and the calcs for the joist at the reduced sections are still working, but my fear is that the weakened joist floor system may have issues in the long run.
Since it is difficult quantify the performance of the floor system of engineered wood joists with a lot of holes drilled through their length, I think that my fix is reasonable considering the cost of the home. What are some of your thoughts?