Suggestion: The question appears to be linked to transformer connections, e.g. Y-Y (secondary neutral grounded only) and ground fault currents. For example, if the transformer has no magnetic phase interlinkage, e.g. shell type or three 1-phase type transformers, then there will be no zero phase sequence current on the secondary under the ground fault condition on the secondary side. However, in a core type unit the fluxes produced by zero sequence currents find a high-resistance path outside the core. Therefore, there will be a somewhat small zero phase sequence current flowing.