Zig-Zag Grounding transformer

Status
Not open for further replies.

tsknan

Electrical
Jan 30, 2009
16
can any body tell how to calculate the capacity (KVA) of a zig-zag grounding transformer ,we are using this to provide ground fault path to 33 KV delta system ,we want to use the secondary of this Tr for Aux load(33KV/415V)
 
Replies continue below

Recommended for you

What's the earth fault current?
Is there a neutral earthing resistor?
How long will an earth fault be allowed to stay on the system?
What KVA do you need for your auxiliaries?

Regards
Marmite
 
What marmite said; more information is needed to arrive at a good answer!
 
The zigzag configuration is only use to protect ungrounded side of power transformer. The capacities it is depend on the load that will be connect to this transformer, because with this kind you have the point of earthing and auxiliary power supply.
 
Our client mentioned there may be impedance issue with Zig-zag transformer. I don't really understand this. Can somebody here shed me some lights on me?

Thanks in advance.
 
I didn't know that Zig Zag made transformers too... Smokin!

Mike McCann
MMC Engineering
 
Another misspent youth!! LOL.
My friends preferred Zig-Zags, just like yours!


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Any health and safety issue to the operators with Zig-zag transformer?
 
Nope. You don't usually visit the transformer often.
 