mls1
Electrical
- Aug 15, 2002
- 133
A post a few years ago discussed the calculations associated with zig-zag grounding transformers. In it one user posted the following:
"You might need to reconsider an almost entirely reactive impedance for the grounding. It is generally considered a bit of a no-no to have reactance grounded systems, due to the problems with power frequency overvoltages under arcing earth fault conditions. I don't recall all the details, but the mining industry in South Africa had some problems with it in the 1970s. There were a few papers in the SAIEE journal - people like a Dr Pretorius at the CSIR were involved with it back then, I think. Eastern Natal Region of Eskom used an NEC / NER combination at 11kV to keep earth fault levels to 300A, and the R componenet was to ensure that the system was not reactively earthed. "
We are involved in a project in which a 22.9kV system with a zig-zag grounding transformer has experienced some surge voltage problems. The zig-zag is directly grounded without a resistance so that minimum ground resistance will be leakage inductance only. I have been searching for the above papers describing possible power frequency overvoltages during arcing earth fault conditions. This seems like a plausible cause if there is phase angle displacement on each arc fault. I did search SAIEE (I am in the USA) but could not find anything that old. Can anyone point me to where I might find the above references or any other references that may cover arcing fault transient voltages on zig-zag grounded systems? Much appreciated!
"You might need to reconsider an almost entirely reactive impedance for the grounding. It is generally considered a bit of a no-no to have reactance grounded systems, due to the problems with power frequency overvoltages under arcing earth fault conditions. I don't recall all the details, but the mining industry in South Africa had some problems with it in the 1970s. There were a few papers in the SAIEE journal - people like a Dr Pretorius at the CSIR were involved with it back then, I think. Eastern Natal Region of Eskom used an NEC / NER combination at 11kV to keep earth fault levels to 300A, and the R componenet was to ensure that the system was not reactively earthed. "
We are involved in a project in which a 22.9kV system with a zig-zag grounding transformer has experienced some surge voltage problems. The zig-zag is directly grounded without a resistance so that minimum ground resistance will be leakage inductance only. I have been searching for the above papers describing possible power frequency overvoltages during arcing earth fault conditions. This seems like a plausible cause if there is phase angle displacement on each arc fault. I did search SAIEE (I am in the USA) but could not find anything that old. Can anyone point me to where I might find the above references or any other references that may cover arcing fault transient voltages on zig-zag grounded systems? Much appreciated!