Hello Folks,
I have a generating station with three 2.5MW gas units. We have high resistance grounding on the gensets and they are connected to 3 wye-delta step up transformers. At high voltage delta side a neutral will be achieved using a zigzag grounding transformer. I am trying to figure out the size for that zig-zag and have following questions.
1. Available fault current changes with time because of subtransient, transient and synchronous impedance of generators. What fault current value should I use to size the zig-zag?
2. If you want to limit the available fault current through zig-zag's internal impedance, how do you calculate that? And how to report it to the manufacturer for biddig?
Thank you in advance for any help.
I have a generating station with three 2.5MW gas units. We have high resistance grounding on the gensets and they are connected to 3 wye-delta step up transformers. At high voltage delta side a neutral will be achieved using a zigzag grounding transformer. I am trying to figure out the size for that zig-zag and have following questions.