Suggestion: Reference:
Donald Beeman "Industrial Power Systems Handbook," 1st edition, McGraw-Hill Book Co., Inc., 1955
Section: Zig-Zag Grounding Transformers on page 347
The Zig-Zag transformer is applied without the neutral resistor. The short-time kVA rating of a grounding transformer is equal to rated line to neutral voltage times rated neutral current. A grounding transformer is designed to carry its rated current for a limited time only, such as 10sec or 1min.
Hence, the transformer is usually about one tenth as large, physically, as an ordinary three-phase transformer for the same rated kVA.
Y-Delta Grounding Transformers
The Y neutral has added resistance and it is grounded. Delta is closed to provide a path for the zero sequence current. The Y-winding must be of the same voltage as the circuit it is which is to be grounded.