I am currently working on the coordination study using SKM power tool analysis. Questions regarding the ZSI settings.
The SKM support told me that I have to input the Trip/Delay time(sec) for the breakers with ZSI module. The manufacturer said that the minimum trip time is 0.1. Please have a look at the attachment. The diagram shows five breakers (U1-utility, G1-Generator, T1-tie, C2 and C4) with the ZSI. I believe I should not input 0.1 sec for all five breakers.
C2 shall trip before U1 or G1 or T1
T1 shall trip before U1 or G1
C4 shall trip before U1 or G1 or T1
So I believe I shall input 0.1 for C2 and C4, 0.15 for T1, 0.2 for U1 and G1. Is that how it works?
I am currently working on the coordination study using SKM power tool analysis. Questions regarding the ZSI settings.
The SKM support told me that I have to input the Trip/Delay time(sec) for the breakers with ZSI module. The manufacturer said that the minimum trip time is 0.1. Please have a look at the attachment. The diagram shows five breakers (U1-utility, G1-Generator, T1-tie, C2 and C4) with the ZSI. I believe I should not input 0.1 sec for all five breakers.