Electricliff
- Oct 15, 2003
- 13
Li-Ion battery manufacturers provide protection circuits, which are often built into their batteries.
These are based on special purpose integrated circuits which control one or two MOSFETs to isolate the battery if the terminal voltage is over or under certain specified voltages. The circuit can also isolate the battery if excessive current flows in or out of the battery.
I need to operate a Li-Ion battery in a hazardous area product.
A standard test used to prove the intrinsic safety of a product is to assume any semiconductor component can fail to a resistance value which will result in maximum power being dissipated in the package. Under these conditions the surface temperature of the package must not exceed certain specified temperatures for the different I.S. classes.
The problem I have is that the devices used on the battery manufacturer's protection board do not pass this test.
I need to mimic the protection board performance using bigger package devices.
They specify an OFF leakage current of less than one microamp for their board !!!!!
I cannot find D-Pac mosfet devices (the minimum package size that will meet the fault mode temperature requirement)with such low leakage figures. But then its not a parameter that appears very often in parametric search engines.
Does anyone have experience of low leakage switching? Am I better looking for MOSFETs or BJTs ?
Operational current levels will not exceed 3 Amps and voltages will not exceed 9 Volts.
Although "HELP!!!!" is not descriptive as a subject heading, it certainly expresses my current status!!!!
Cliff %-)
Cliff %-)