Steam flow rate (loss) through top of condensate tank 1
engoz
5
Hi there,
I have two questions here but the first and most important is I'm trying to find out the flow of steam from the top of a return condensate tank from a sugar mill pan area so I can work out the condenstae loss. The pressure in the water tank is 75kpa and their is an open 6 inch gate valve on top of the tank which lets out the steam from the water.
The second is I want to put some sort of steam trap on this 6 inch outlet pipe to save this condensate loss. Is this a possibility for this application?
Thanks in advance,
Use the line size and differential pressure between the tank and atmosphere to calculate the steam flow.
You might try using a heat exchanger on the vent, if you have a use for the recovered heat. I think you'll find the steam flow isn't as much as it appears. In any event, it'll all come down to economics.
Be VERY careful if you're considering installing something like a trap on this vent line. All a trap is, is an automatic valve. You could pressurize this tank to dangerous levels, or back condensate up your process due to increased back-pressure, causing problems there. The tank will need to be vented for the condensate pumps to work.
Thanks TBP,
Have you also got an actual formula for working out the steam flow?
Two thin publications I find very useful are "Technical Paper No. 410" by Crane, and "Hook-Ups" by Spirax Sarco.
In the Crane literature, look in chapter 3, page 22. Another approach is to use a table in "Hook-Ups", which shows the percentage of flash steam from given pressures to atmospheric. (In the 11th edition, the table is on page 41.) The table shows 2.9% of condensate at 10 PSIG will flash to steam when dropped to atmospheric pressure.