What jmiec may be suggesting is using the stiffners as a sort of cantilever arm that extends out to the compression flange. This works as long as there is a sort of moment connection between the end of the stiffner and some outside bracing element.
An example: You have a sky walk that is comprised of two 36" deep wide flanges spaced, say, 8 feet apart. The deck of the skywalk is a steel channel, metal deck, concrete slab assembly with the channels spanning from bottom chord of WF to bottom chord....i.e. the deck is set down low and the WF beam compression flanges are about 3 feet above the deck....with no lateral bracing.
You can use vertical web stiffners, rigidly attached to the cross channels such that you have an effective, rigid, "U" shape comprised of vertical stiffner, horizontal channel, and then vertical stiffner.
Thus, the stiffners can laterally resist the lateral buckling of the top flanges because of their rigid connection to the deck channels.