Full Length Reinforcing in Large Diameter Pier?

Status
Not open for further replies.

mrengineer

Structural
Feb 11, 2002
157
For a 5' diameter straight shaft drilled pier, combination friction and end bearing, lengths 70-90', would you consider dropping off the vertical reinforcing at some point? Surrounding soils are capable of providing lateral support for the entire length of the pier.
 
Replies continue below

Recommended for you

I always look at the bending moment from the lateral load analysis and take it past the curve. If there is uplift, you'll need to install a dywidag bar almost full length.
 
We will generally will extend reinforcement 10 to 12 feet or until any bending moment might die out.
 
I once tried to optimize the reinforcing by stopping it part ways down the shaft. The Geotechnical Engineer caught it and notified me that he was counting on a fully reinforced shaft for uplift. It was right there in the Geotechnical Report if I would of been awake enough to notice it.
Anyways, another reason to be careful before you stop the reinforcing.
 