GSU transformer connection 1

Status
Not open for further replies.

Viceng

Electrical
Nov 22, 2005
24
Hello,
I was wondering if someone could suggest pro's and con's to the following configuration I have seen at a hydroelectric generating facility:

Generator: High resistance grounded

GSU trasformer: ungrounded wye (4.2kV)/ delta (69kV).

There is one station service transformer on the 4.2kV system (delta-grounded wye 4.2kv-600V). Apart from this the rest of the 4.2kV system is only instrument transformers and some surge arrestor and capacitors.

Thanks!
 
Replies continue below

Recommended for you

Something in particular you are concerned about?
 
Well to be quite honest: My inexperience in the matter and the fact that I rarely see this connection.

I am guessing that that one would go for this connection over a delta-delta MPT as the delta-wye is more readily available?

Cheers.
 
Probably started with a requirement that the 69 kV connection be delta, for whatever reason. The generator should be grounded via high resistance grounding, normally at the generator. This rules out a grounded wye connection on the low side of the GSU. So the generator grounding is OK for protecting the generator, the aux transformer delta-wye works out OK. The ungrounded wye is a bit non-typical - perhaps it had already been ordered before it was determined that it shouldn't be grounded.

 