gepman
Electrical
- Mar 26, 2007
- 364
I was asked to look at the energy consumption of a small (55,000 sq. ft) conditioned warehouse (72 deg. F) in a mild climate (Los Angeles Area). The warehouse has six 30 ton package units with economizers and exhaust dampers. What I don't understand is that it has twelve 42"x48" gravity hoods (about 6" screen opening around the perimeter of each). I assume that these are for fresh air requirements for the use of some forklifts (maybe six forklifts max.). I have a couple of questions:
1) Does anyone have a good rule of thumb (or more rigorous method) of determining the amount of outside air that is coming in through these gravity hoods? I looked in the ASHRAE Fundamentals but the natural ventilation calculations looked very complicated with not much hope of being very accurate even for all of the trouble. At the moment my best guess is looking at an equivalent Greenheck gravity hood flow at the lowest pressure drop (.057"), about 6600 cfm. I know that with the package units running it won't exactly be natural convection.
2) Does anyone know of any requirements for ventilation for forklifts? It would seem that closing off the uncontrolled air entry of the gravity hoods and using demand control ventilation by measuring CO2 and CO and controlling the OA to the package units would be better.
I might also suggest using electric forklifts which most of the cold storage warehouses use.