Portal Column Restraints

Status
Not open for further replies.

Vinny7

Structural
Jan 27, 2003
54
Hi,

If a portal is clad in blockwork to eaves (no sheeting rails) can it be assumed the blockwall (215MM thk.) between the flanges (305X165 Universal Beam) be considered as providing restraint to the column compression flange at the bottom of the rafter haunch. IF not has anyone any suggestions? Note, the eaves tie will probably be at higher level to suit the roof and wall bracing.
 
Replies continue below

Recommended for you

If I understand your scenario correctly, I would not rely on the block wall for lateral restraint of the compression flange of the steel beam unless the wall is perpendicular to the beam.

That being said, the wall is parobably parallel to the beam, so, could you add some diagonal angle bracing from the bottom flange of gthe steel beam to the underside of the floor/roof diaphragm system to brace the bottom chord?

Mike McCann
McCann Engineering
 
Thanks very much,as you stated first the column is in the external wall of a small warehouse and connected to a roof rafter with haunch(the wall is perpendicular to the column and beam running between columns) but as the blockwork do not fully fill the web I am looking for advise or comments?

Thanks
 
The top of the block wall needs to be braced, and that member can be used to brace the portal frame at the knee.
 
I don't think there will be a problem with the wall itself. I am thinking of anchor bolting angle beackets to the block wall either side of the column at the bottom of the haunch. This should provide the restrains required.
 