JoseAcevedo
Mechanical
- May 25, 2007
- 13
I have to design a tank and the customer specify an internal design pressure of 0.2 psi. The custumer also specify that the tank must have an open vent with flame arrestor and in case of flame arrestor obstruction the customer require additionally a Pressure & vaccumm relief valve with flame arrestor too. The tank diameter is lesser than 40 feet thus an emergency vent it is required too.
In our case we have the following:
1.- The operation pressure of the open vent with flame arrestor (almost atmospheric).
2.- The Operation pressure of Pressure & vaccumm relief valve with flame arrestor setting at aproximatetelly 2" w.c.
3.- the operation pressure of the emergency vent setting at aproximatelly 4" w.c.
My question is: What is the notmal operation that we have consider for the tank, the number 1 or 2?
In our case we have the following:
1.- The operation pressure of the open vent with flame arrestor (almost atmospheric).
2.- The Operation pressure of Pressure & vaccumm relief valve with flame arrestor setting at aproximatetelly 2" w.c.
3.- the operation pressure of the emergency vent setting at aproximatelly 4" w.c.
My question is: What is the notmal operation that we have consider for the tank, the number 1 or 2?