I've been practicing for 26 years and never thought about this question recently posed to me by a contractor. Why do we need a "granular capillary break" if there is a vapor barrier? I can see the need if there is groundwater present; the capillary break will provide a conduit for ground water to drain to a lower level. Hydrostatic slabs are another subject altogether and beyond this discussion. I'm concerned about normal commercial and residential slabs where groundwater is not present.
I've been researching the subject and cannot find an answer to the question posed above. Most "authorities" indicate that a capillary break and a vapor barrier are required. The authorities also state that the capillary break won't stop vapor, only water. And we're all familiar with the controversy of whether the vapor barrier goes below or above the granular fill; it is well documented with authorities on both sides of that argument, so let’s not get into that question.
ACI 302.1R-04 Concrete Floor and Slab Construction, paragraphs 4.1.4, Base Material, recommends "a clean, fine-graded material with at least 10 percent to 30 percent of particles passing the No. 10 sieve ..." I copied that verbatim and have been using it in my General Notes for years. All this time I thought was that this was a spec for the "granular fill capillary barrier", but now I realize that it could not be with that many fines. I believe this is merely a good compactable base to pour a slab on. In fact, it is not a good capillary barrier at all.
In a post from “fattdad” on 7-6-06, he analyzed a “dense-graded aggregate (i.e., minus 3/4-in with about 5 percent passing the 200 sieve - D10 of about 0.15 mm) for the "capillary break" [typically used] beneath industrial floor slabs”. He concludes: “Looking at Terzaghi's book, the standard equation for capillary rise is Hc=c/(e*D10) using consistent units, where C is in the range of 0.1 to 0.5 cm. When I use this equation for the dense-graded aggregate, the calculated range for capillary rise is somewhere in the range of 23 to 115 cm (9 to 45 inches). As you can imagine this does not seem to offer a very effective "capillary break" when a typical layer thickness is 6 inches.
“
There is new ACI document ACI 302.2R-06 Guide for Concrete Slabs that Receive Moisture-Sensitive Flooring Materials. There is no mention of a capillary break in that document. They speak of the advantages of a "granular base" over the vapor barrier (7.2.1) acting as a blotter, but do not call it a capillary break. I don't believe it is a capillary break. I believe it is the same granular base described in ACI 302.1R above, which is more of a structural base than a capillary break.
So I ask, is there really a need for a capillary break? Is the term being misused? Is it really a compactable granular base used as a blotter for bleed water?
A capillary break is supposed to stop moisture from “wicking” up to the slab. We have begun specifying good quality vapor barriers, with very low perm ratings, taped joints, boots around pipe penetrations, etc. I wonder, with a good vapor barrier is there any need for a capillary break? Does it really matter if the soil under the vapor barrier is moist?
I've been researching the subject and cannot find an answer to the question posed above. Most "authorities" indicate that a capillary break and a vapor barrier are required. The authorities also state that the capillary break won't stop vapor, only water. And we're all familiar with the controversy of whether the vapor barrier goes below or above the granular fill; it is well documented with authorities on both sides of that argument, so let’s not get into that question.
ACI 302.1R-04 Concrete Floor and Slab Construction, paragraphs 4.1.4, Base Material, recommends "a clean, fine-graded material with at least 10 percent to 30 percent of particles passing the No. 10 sieve ..." I copied that verbatim and have been using it in my General Notes for years. All this time I thought was that this was a spec for the "granular fill capillary barrier", but now I realize that it could not be with that many fines. I believe this is merely a good compactable base to pour a slab on. In fact, it is not a good capillary barrier at all.
In a post from “fattdad” on 7-6-06, he analyzed a “dense-graded aggregate (i.e., minus 3/4-in with about 5 percent passing the 200 sieve - D10 of about 0.15 mm) for the "capillary break" [typically used] beneath industrial floor slabs”. He concludes: “Looking at Terzaghi's book, the standard equation for capillary rise is Hc=c/(e*D10) using consistent units, where C is in the range of 0.1 to 0.5 cm. When I use this equation for the dense-graded aggregate, the calculated range for capillary rise is somewhere in the range of 23 to 115 cm (9 to 45 inches). As you can imagine this does not seem to offer a very effective "capillary break" when a typical layer thickness is 6 inches.
“
There is new ACI document ACI 302.2R-06 Guide for Concrete Slabs that Receive Moisture-Sensitive Flooring Materials. There is no mention of a capillary break in that document. They speak of the advantages of a "granular base" over the vapor barrier (7.2.1) acting as a blotter, but do not call it a capillary break. I don't believe it is a capillary break. I believe it is the same granular base described in ACI 302.1R above, which is more of a structural base than a capillary break.
So I ask, is there really a need for a capillary break? Is the term being misused? Is it really a compactable granular base used as a blotter for bleed water?
A capillary break is supposed to stop moisture from “wicking” up to the slab. We have begun specifying good quality vapor barriers, with very low perm ratings, taped joints, boots around pipe penetrations, etc. I wonder, with a good vapor barrier is there any need for a capillary break? Does it really matter if the soil under the vapor barrier is moist?