Parkpower
Electrical
- Jan 18, 2009
- 18
Hello everyone,
We are doing grounding simulation and calculating grounding resistance, touch potential etc. The incoming 60kV step down to 5.5KV and the 60kv system is high resistance grounded and Neutral grounding resitance is rated 200A 10ohm 1s. The maximum fault level at 30KV bus is 25kA.
When we calculate grounding potential, what is the phase ground short circuit current ? 200A OR 25kA?
Thanks,
Hery
We are doing grounding simulation and calculating grounding resistance, touch potential etc. The incoming 60kV step down to 5.5KV and the 60kv system is high resistance grounded and Neutral grounding resitance is rated 200A 10ohm 1s. The maximum fault level at 30KV bus is 25kA.
When we calculate grounding potential, what is the phase ground short circuit current ? 200A OR 25kA?
Thanks,
Hery