We have a GE 32000 Hp synchronous motor and we would like to measure the rotor stator airgap. Is it best to use long feeler gauges or just do point measurements around the rotor?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
API 1068 said:Centering of the rotor within the stator should be checked, whenever permitted by the machine
construction, by both stationary gap and rotating gap feeler gage readings at both ends of the motor. Readings should be taken at not less than three points 90° apart around the rotor periphery. In the stationary check, feeler gages are inserted successively at the separate points and the values are recorded. In the rotating check, the gages are left at one location and the rotor is turned in 90°
steps, noting the reading at each step. This test can reveal an eccentric rotor that may go undetected
by the stationary test. Readings shall not exceed a 10% deviation from the average at each end.
(See API 541-1995, Section 2.4.7.16.)What I described imo accomplishes the intent of both tests.
From their discussion you see as we all know there is stationary eccentricity (basically lack of centering) or rotating eccentricity 9typically runout).
If rotor iron runout is small for example < 0.002", then probably the stationary test is good enough.
If rotor iron runout is 0.005" (as is common for our very large motors), then you see the rotor TIR is on the same order as the 10% airgap acceptance criteria... tough to ignore it imo.
At any rate, it was a good clarification. Certainly rotating rotor is not required for smaller motors and many standards. Some standards and customers (like me) prefer it for reasons discussed above
=====================================