Can anybody explain, what is the idea behind having 100% insulation level and 133% insulation level in testing XLPE, EPR medium voltage cables?
Thank you
Thank you
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
IEEE-141/1993 said:"There are three levels of conductor insulation for MEDIUM-VOLTAGE CABLES: 100, 133, and 173% levels. The solidly grounded system permits the use of 100% insulation level. When the fault on the other system will raise the system voltage above normal during the time of the fault, 133% insulation level should be specified if the fault is cleared within one hour. When the fault will remain on the system for an indefinite time, 173% voltage level insulation=====================================