ML1400 analog outputs

Status
Not open for further replies.

hrcooper

Electrical
Aug 31, 2011
36
According to the programming guide, output words 4 and 5 have the analog values. So how do you put values in there? I know..its a simple question but...I cant create a data file for O4 and O5, so how do you control the two analog outputs?
 
Replies continue below

Recommended for you

not familar with ML1400, probably uses the slc500 instruction set

example N7:0 is your word value of where you did some final move from what ever algorithm that your using.

so just do below
Copy statement

COP N7:0 O:4
 
In RsLogix500, there is the MOV instruction, and I had tried that but its asking for word level address, and that makes sense since the outputs are binary.

So whats next...
 
OK, got it to work.

O:0.4 holds the value 0-4096 for a 0-10V output.

Sometimes the obvious...isnt so obvious....
 