brownstonestruct
Structural
- Apr 11, 2012
- 2
Other NYC structures guys may be familiar with this situation. I have a project combining two 5-story brownstones, knocking out the middle party wall, re-framing each floor level and adding a new conc/cmu elevator core (13'x22'). Now the shaft needs to be designed to resist the total seismic lateral forces, which, after based on NYC seismic code, the factored design moment at base= 8,400 k-ft. So far my numbers show that I can get a 10" thick conc. wall to work with (8)#9 bars at the corners. Now as I move up the shaft, the architect wants 8" CMU walls. So, I'm looking at switching to 8" CMU at the 3rd floor where the design moment drops to around 5,000 k-ft which will require roughly (6) #6 bars at each of the corners of the shaft.
Sorry for the long story but, for you veterans of CMU and shear wall design out there, is this asking way too much from a CMU elevator shaft? Is it possible to bundle the #6 bars in 8" CMU?
Any and all input is appreciated..