acog
Electrical
- Jul 30, 2010
- 31
Hi,
I have a supply substation with an earth grid, and a long cable (e.g. 10km) which supplies some equipment sitting on its own earth grid. I have a good understanding of the earth grid impedances of both the feeding substation and the remote equipment earth grid.
The cable which feeds the remote equipment is a three core XLPE compressed strand Aluminium cable where each core is screened by copper strand as per the image below.
My problem is that I need to calculate the percentage of current which enters the soil and the percentage of current which returns via the cable screen under an earth fault scenario at the remote equipment. The project is in the design phase so I can not test via injection.
I was intending to solve this problem by calculating the cable screen zero sequence self impedance (Zs) and mutual impedance (Zm) then using the following formula to work out the current in the remote earth grid.
Remote Ground Grid Current = Total Fault Current Available at Remote Source * (Zs - Zm)/(Zs + 3*Rg)
Where Rg = the remote earth grid resistance + the substation earth grid resistance.
However I can't find any method to work out the GMR (and hence the mutual impedance) for the cable screen because the screens are around the phase conductors. The only method I can find involves a cable with a screen which encircles all three cores, and I am not sure if this is applicable here.
The cable manufacturer has supplied 'Zero Sequence Resistance' and 'Zero Sequence Reactance', however I am not sure as to whether I can use these numbers for the cable screen impedance calculation.
Since the cable runs are long and there will be good inductive coupling of the cores and screens, I don't want to just use the DC screen resistance value.
Any help would be greatly appreciated.
Andy
I have a supply substation with an earth grid, and a long cable (e.g. 10km) which supplies some equipment sitting on its own earth grid. I have a good understanding of the earth grid impedances of both the feeding substation and the remote equipment earth grid.
The cable which feeds the remote equipment is a three core XLPE compressed strand Aluminium cable where each core is screened by copper strand as per the image below.

My problem is that I need to calculate the percentage of current which enters the soil and the percentage of current which returns via the cable screen under an earth fault scenario at the remote equipment. The project is in the design phase so I can not test via injection.
I was intending to solve this problem by calculating the cable screen zero sequence self impedance (Zs) and mutual impedance (Zm) then using the following formula to work out the current in the remote earth grid.
Remote Ground Grid Current = Total Fault Current Available at Remote Source * (Zs - Zm)/(Zs + 3*Rg)
Where Rg = the remote earth grid resistance + the substation earth grid resistance.
However I can't find any method to work out the GMR (and hence the mutual impedance) for the cable screen because the screens are around the phase conductors. The only method I can find involves a cable with a screen which encircles all three cores, and I am not sure if this is applicable here.
The cable manufacturer has supplied 'Zero Sequence Resistance' and 'Zero Sequence Reactance', however I am not sure as to whether I can use these numbers for the cable screen impedance calculation.
Since the cable runs are long and there will be good inductive coupling of the cores and screens, I don't want to just use the DC screen resistance value.
Any help would be greatly appreciated.
Andy