•I came across these bushings on a Delta/Wye 2 winding transformer recently. They are separate from the H1-H3 and X0-X3 bushings. Are these core grounds? Is there any reason why there are two brought out to the top of the tank? One was grounded and one was ungrounded as shown.
•Also, when shorting low side bushings for various tests (jumpered X1-X2-X3), it is often recommended that an additional jumper is included from X3 back to X1. Is there a reason for this? Is it just for redundancy?
•When performing TTR, winding resistance, and bushing CT tests on three phase Dyn two-winding and auto transformers, is it recommended to leave the neutral bushing connected to ground or left floating?
Thank you.
•Also, when shorting low side bushings for various tests (jumpered X1-X2-X3), it is often recommended that an additional jumper is included from X3 back to X1. Is there a reason for this? Is it just for redundancy?
•When performing TTR, winding resistance, and bushing CT tests on three phase Dyn two-winding and auto transformers, is it recommended to leave the neutral bushing connected to ground or left floating?