Hi i have torsion in RC T-beam, If the Flange and web of t beam are not cast at the same time. Can i consider torsion on concrete to the whole t beam or i should consider concrete torsion on the pile cap or the flange only,
also can any body give and example how to calculate torsion calc for t beam.
Torsion calculations are based on the area enclosed within the transverse reinforcement.
If I am relying on the concrete capacity for torsion, is it mandatory that I consider area of concrete only if enclosed by stirrups.
Below a certain demand threshold, you can use unreinforced concrete.
One needs to be cognizant of proportions with things like this. If the proportions that you've sketched are accurate, what you've got here is a stem wall loaded in out of plane flexure and cantilevered from a rectangular grade beam in torsion. As such, I would not include the stem in your torsion resistance model. The two pour sequencing is irrelevant in my opinion.
As the others above have noted, once you're reached Tcr, then the concrete resistance to torsion is reduced to zero causing all torsion to be resisted by the reinforcing. Therefore only the reinforcing cage area can be used to determine torsion resistance.