Kyle VWVE27 Recloser, grounding issues.

Status
Not open for further replies.

Sn00ze

Electrical
Jan 16, 2013
176
Hello,

We have a client that wants to change an Old Cooper Form 4C controller for a SEL-351R to control a Recloser via a 14-pin serial cable in a small 25kV feeder in Canada.

My issue is that Kyle manual say it is star pointed and grounded inside the recloser enclosure (unable to confirm until outage) but the SEL-351R manual says it is grounded in both the recloser enclosure and the SEL-351R enclosure. Any one has any experience with these reclosers? Has anyone ever seen CT starpoint (K-M-L) being grounded in two places like this before?

Cooper Form 4C Enclosure (existing)


Kyle Manual
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1443645345/tips/Cable_35_Breakouts_Connections_in_Controller_Module_jahrh9.pdf
[/url]
Kyle_VWVE27_Recloser_Manual_Page13_hsaqyv.jpg


SEL-351R manual
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1443645360/tips/Pages_from_351R_QS-CD_20070802_camq1x.pdf[/url]


Regards.
 