Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

High Speed Fuses Type question 2

Status
Not open for further replies.

lukin1977

Mechanical
Jan 19, 2009
397
I am looking for 3 high speed fuses type aR . I found a local supplier of high speed fuses but fuse type gS

Does anybody knows the difference between aR and gS fuses?

WhatsApp_Image_2016-08-11_at_11.14.27_xpehb7.jpg


WhatsApp_Image_2016-08-11_at_11.08.41_p147ye.jpg


They are installed on the 3 input lines of a DC Drive
 
Replies continue below

Recommended for you

The first image is a part-range backup fuse (designated by the 'a') for short-circuit protection only. The second image is a full-range fuse (designated by the 'g') for overcurrent and short-circuit protection.

From the internet -

Class aR, gR and gS
Traditionally high speed fuses have only been used for short circuit protection, another device in the circuit protects against overload. Fuses only intended for short circuit protection are called class aR. Recent technological developments have made it possible to combine both short circuit protection and overload protection into the same fuse, class gR.

Class gR and gS offer superior protection compared to class aR. Class gR/gS fuses can often direct replace class aR fuses, however a class gR/gS fuse shall never be replaced by a class aR.
 
Scotty doesn't say it explicitly, but he meant to say that you can use the Sitor fuses. SITOR BTW stands for SIlizium stromTOR, where Stromtor means "current door".

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
by the way, the 3 x 200A aR fuses were "burned" because of heavy sparking on a DC motor commutator caused by a loose brush
 