MDANCE
Electrical
- Dec 17, 2016
- 6
Hi guys, I will start with I am not a Engineer but work as a HV ( LV to 33kv ) distribution designer and have a question for the knowledgeable engineers on here. I have recently upgrade a 3 tank 3 phase star connected 33kv voltage regulator site from 200A regs ( 22kv rated) to 300A regs( 22kv rated )... When comissioned one of the regs had a growling/vibrating noise being emitted. The decision has been made to put them in by-pass and take them out of service to remove offending unit for testing and maintenance... Our zone substations group was arranging to put one of the old 200A reg units back up in place of the 300A being removed for testing as to keep the site "online". I've put a stop on this as I have concerns about the differing impedences of the 200 and 300 amp units and the effect this will have on the common star point. I feel there will be an out of balance created and cause a rise on the earthing system connected to the star point along with other issues that are beyond my ability to figure out. Our zone subs engineers "thinks" it will work but couldn't give me any concrete evidence it would. Has anyone had experience in this situation and could anyone explain the full effects that could happen to the sub-transmission system if the 200A was put in place... Thank you in advance for any responses.