I have existing (30+ year old) 2-span PT beams (5'0" deep x 2'6" wide) that requires significant strengthening over the interior support (negative moment) for additional loadings for a proposed roof recreation deck.
The upturn can be integrated into the completed rec deck as a new pedestal system (of several feet in height) will be provided.
I have used ACI 318-14 to check horizontal shear transfer (composite action of existing beam to new CIP upturn) for a magnitude equal to the total tensile capacity of the added rebar.
I checked interface shear and shear reinforcing is required, via shear-friction across an intentionally 1/4" magnitude roughened joint of 24" width.
I have used only #3 reinforcement to assist with a reduced straight bar development lengths (ld=12" for #3) into the existing concrete (via epoxy etc), and #3 also results in a reduced hooked development length (ldh=6.5" for #3) above the interface.
I would usually detail a third row of reinforcement down the centerline of the beam (across the 24" upturn width), HOWEVER, there is existing PT tendons that I wish to avoid drilling through, so I only have 2#3 over the 24" width.
Any thoughts/comments of the following detail WITHOUT a center row of #3 interface reinforcing?
The upturn can be integrated into the completed rec deck as a new pedestal system (of several feet in height) will be provided.
I have used ACI 318-14 to check horizontal shear transfer (composite action of existing beam to new CIP upturn) for a magnitude equal to the total tensile capacity of the added rebar.
I checked interface shear and shear reinforcing is required, via shear-friction across an intentionally 1/4" magnitude roughened joint of 24" width.
I have used only #3 reinforcement to assist with a reduced straight bar development lengths (ld=12" for #3) into the existing concrete (via epoxy etc), and #3 also results in a reduced hooked development length (ldh=6.5" for #3) above the interface.
I would usually detail a third row of reinforcement down the centerline of the beam (across the 24" upturn width), HOWEVER, there is existing PT tendons that I wish to avoid drilling through, so I only have 2#3 over the 24" width.
Any thoughts/comments of the following detail WITHOUT a center row of #3 interface reinforcing?