P1ENG
Structural
- Aug 25, 2010
- 237
Let's say I have 3" of 5000 psi concrete (3" topper of a 6" thick deck), such that le=da=3". I want to put plates on both sides and bolt through the concrete with 3/4" A36 rod to connect the plates. The closest edge distance is 20.5" (ca1). I am using ACI 318-14. Avco (17.5.2.1) is very large because of the large edge distance and Avc is very small because of the 3" thickness. So my Avc/Avco = 0.098. Vb (17.5.2.2) is equal to 52.5 kip [9*sqrt(f`c)*ca1^1.5 -OR- 7*(le/da)^0.2*sqrt(da)*sqrt(f`c)*ca1^1.5]. My Vcb ends up being 5.12 kip. This seems pretty small for such a large edge distance. Am I missing something? Am I shooting myself in the foot by only using the continuous 3" thickness of the topper? There is WWM in the topper, should I be including that somehow?
It is a little crude since it is preliminary, but below is my math.
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant
It is a little crude since it is preliminary, but below is my math.
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant