lewismg
Chemical
- Feb 6, 2003
- 4
I am sizing a control valve for a reflux system that has been poorly designed. The valve controls temperature in the column (cascaded to flow) by throttling flow downstream of a centrifugal pump. Unfortunately, an inappropriate pump has been bought for this application and it will be operating inefficiently at the left side of it's curve. Also, the dynamic losses in the system are low so the system curve is very flat. Results in the following Cv cases:
Min Cv Case: Q = 5.31 GPM, dP = 48.2 psi
Normal Cv Case: Q = 10.6 GPM, dP = 45.8 psi
Max Cv Case: Q = 13.8 GPM, dP = 45.1 psi
My contention is that because the difference in pressure drop is so small, the pump will be sensitive to small changes in control valve pressure drop and will float along it's curve. Can a system like this be controlled?
The 30% CV pressure drop / dynamic loss (or 15 psi) rule of thumb ensures that the pressure drop across the CV is not too low. Is there a similiar rule for a case in which CV pressure loss >> system dynamic losses?
Any help is appreciated.
Mike
Min Cv Case: Q = 5.31 GPM, dP = 48.2 psi
Normal Cv Case: Q = 10.6 GPM, dP = 45.8 psi
Max Cv Case: Q = 13.8 GPM, dP = 45.1 psi
My contention is that because the difference in pressure drop is so small, the pump will be sensitive to small changes in control valve pressure drop and will float along it's curve. Can a system like this be controlled?
The 30% CV pressure drop / dynamic loss (or 15 psi) rule of thumb ensures that the pressure drop across the CV is not too low. Is there a similiar rule for a case in which CV pressure loss >> system dynamic losses?
Any help is appreciated.
Mike