GENERAL: wind power plants (WPP) are characterized by feeders with larger capacitance than conventional OH lines. The WPG also generates significant harmonic distortion and exposed to transient overvoltages, transformer saturation, power factor, reactive power, and voltage control issues.
The optimal design of the 33 kV and 0.4kV systems can be achieved with the proper selection of the neutral grounding/earthing auxiliary transformer. It is recognized that neutral grounding can be achieved in variates of connections such as YΔ, ZNyn, ZNdyn, ZNzn.
The best performance and cost for each application should be evaluated as well as the familiarity and experience for this application. In the USA, the most frequent application for a neutral/grounding transformer is Dyn and simple zig-zag unit. In Europe, the experience gained in several offshore projects favors the use of ZNdyn neutral grounding transformer for WPP.
Transformer Dyn is not a grounding transformer. Here are some potential issues:
1.1 During SLG fault, cause high phase-to-neutral voltages on the unfaulted phases.
1.2 Load unbalances can also cause neutral shifts and overvoltages.
1.3 The low zero sequence impedance of ZNyn & ZNdyn is an efficient way to mitigate the triplen harmonic (3
rd, 9
th, 15
th...)
This might be a project requirement and a potential safety issue in a metallic platform for an offshore substation application. In general, the ground source facilitates the ground protective device coordination and monitoring of the system in the event of SLG fault.
The 30
o phase shift of the Dyn by itself usually is not a problem. Special attention needs to be observed for connection to a standby generator to the LV bus for black-start, emergency or parallel mode.
I found the enclosed information very informative