10.5 of ACI 318-11 shows the folloing (see image below):
ACI 318-11 in section 10.5.4 states "For structural slabs and footings of uniform thickness, As,min in the direction of the span shall be the same as that required by 7.12.2.1. Maximum spacing of this reinforcement shall not exceed three times the thickness, nor 18 in."
R10.5.4 in the commentary mentions the following: The minimum reinforcement required for slabs should be equal to the same amount as that required by 7.12.2.1 for shrinkage and temperature reinforcement. Slabs-on-ground are not considered to be structural slabs in the context of this section, unless they transmit vertical loads or lateral forces from other parts of the structure to the soil. Reinforcement, if any, in slabs-on-ground should be proportioned with due consideration of all design forces. Mat foundations and other slabs that help support the structure vertically should meet the requirements of this section.
Would this mean that a minimum flexural reinforcement, as stated in 10.5.4 of ACI 318-11, needs to be satisfied along with the temp & shrinkage reinforcement for mat foundations? Or is this just referring to flexural members, like beams?
I ask because that seems to contradict what is stated in Section 15.10.4 of ACI 318-11. Section 15.10.4 states "Minimum reinforcing steel in nonprestressed mat foundations shall meet the requirements of 7.12.2 in each principal direction. Maximum spacing shall not exceed 18 in."
Also, PCA states the following (see image below):
Could some please clarify this?
Comments/suggestions are appericated.
ACI 318-11 in section 10.5.4 states "For structural slabs and footings of uniform thickness, As,min in the direction of the span shall be the same as that required by 7.12.2.1. Maximum spacing of this reinforcement shall not exceed three times the thickness, nor 18 in."
R10.5.4 in the commentary mentions the following: The minimum reinforcement required for slabs should be equal to the same amount as that required by 7.12.2.1 for shrinkage and temperature reinforcement. Slabs-on-ground are not considered to be structural slabs in the context of this section, unless they transmit vertical loads or lateral forces from other parts of the structure to the soil. Reinforcement, if any, in slabs-on-ground should be proportioned with due consideration of all design forces. Mat foundations and other slabs that help support the structure vertically should meet the requirements of this section.
Would this mean that a minimum flexural reinforcement, as stated in 10.5.4 of ACI 318-11, needs to be satisfied along with the temp & shrinkage reinforcement for mat foundations? Or is this just referring to flexural members, like beams?
I ask because that seems to contradict what is stated in Section 15.10.4 of ACI 318-11. Section 15.10.4 states "Minimum reinforcing steel in nonprestressed mat foundations shall meet the requirements of 7.12.2 in each principal direction. Maximum spacing shall not exceed 18 in."
Also, PCA states the following (see image below):
Could some please clarify this?
Comments/suggestions are appericated.