Hi folks, I am looking for some assistance with a hydronic system that serves our chiller plant. We have 3 chillers served by two dry coolers. The condenser loop is a closed loop system and uses 30% ethylene glycol.
The loop temperature is 45F in the winter and goes as high as 110F in the summer.
The condenser loop is equipped with a AMTROL bladder type expansion tank (see cut sheet attached). The expansion tank is installed close to the inlet of the pumps. The air side pressure at the expansion tank reads 11-12 PSI yet the pressure gauge where the expansion tank connects to the system reads -7 PSI when the pumps are running. When the pumps are off the pressure reading is 0 to 4 PSI
I don’t understand why there is a large discrepancy in pressure readings. Literature indicates that the pressure on air and liquid side of the expansion tank should be identical or close to each other.
The condenser pumps are not operating smoothly and are very noisy, most likely they are cavitating. The fact that the suction header is negative results in air being drawn in through the glycol feeder and the air vents, so we’ve isolated both devices with ball valves.
I have also attached a mechanical schematic. We've tested for leaks in the system and haven't found any.
Any ideas what to look for next? Also reached out to Amtrol but they haven't been very helpful.
The loop temperature is 45F in the winter and goes as high as 110F in the summer.
The condenser loop is equipped with a AMTROL bladder type expansion tank (see cut sheet attached). The expansion tank is installed close to the inlet of the pumps. The air side pressure at the expansion tank reads 11-12 PSI yet the pressure gauge where the expansion tank connects to the system reads -7 PSI when the pumps are running. When the pumps are off the pressure reading is 0 to 4 PSI
I don’t understand why there is a large discrepancy in pressure readings. Literature indicates that the pressure on air and liquid side of the expansion tank should be identical or close to each other.
The condenser pumps are not operating smoothly and are very noisy, most likely they are cavitating. The fact that the suction header is negative results in air being drawn in through the glycol feeder and the air vents, so we’ve isolated both devices with ball valves.
I have also attached a mechanical schematic. We've tested for leaks in the system and haven't found any.
Any ideas what to look for next? Also reached out to Amtrol but they haven't been very helpful.