Hi,

I am trying to figure out torsional rigidity for the below connection type. Where can I find reference for calculating torsional rigidity for such a connection?

I am trying to decipher the requirement in AISC for seismic connection. This below connection is recommended in AISC more for a beam which has a diaphragm. When there is no diaphragm at the beam level the connection must meet torsional rigidity requirement. Trying to understand if I can still meet torsional rigidity with such a connection.




Document1_ushy1m.jpg
 
I would do the same calcs as for a beam. Treating the plates as beams.
 
BAGW,

This connection has the torsional rigidity of a limp spaghetti noodle, well past al dente. You must restrain the flanges from warping to restrain the I section from rotating torsionaly. This joint is even worse since the flanges are not even connected. A rectangular or pipe section would be a lot more effective.

Jim
 
Jim for the win!

The goal with torsional rigidity is to try and make everything "close-celled" or tubes. Then the warping component basically nosedives out of the equation.
 
For a rectangle, J = b*t^3/3. So there is some torsional rigidity, but not much.

DaveAtkins
 
To expand a bit further on Dave's equation, for multiple pieces in a cross section: J= ∑(bt3/3)

where:

b=length of each cross-sectional element
t=thickness of each cross-sectional element

This formula is (of course) a approximation....but I have found it to be sufficient in most cases.
 
BAGW said:
I am trying to decipher the requirement in AISC for seismic connection.

Which particular requirement in AISC 341-16? The bar is higher for some applications than others.

With regard to your torsional stiffness/flexibility here, there are a few considerations:

1) St. Venant Torsion in the plates per Dave and goutam.

2) Warping torsion in the plates.

3) Prying action in bolts and local flexibility of the beam webs of both the supporting and supported beams.

4) St. Venant Torsional in the supporting beam.

5) Warping Torsion in the supporting beam.

In a high seismic application without a diaphragm, I'd expect you to need discrete bracing of both flanges near the splice as well as a torsional robust splice connection. But, again, much depends on what AISC provision we're talking about.
 
@ KootK

I am referring to AISC 360-10. Thanks
 
BAGW said:
I am referring to AISC 360-10.

Come now, I know that. I'm asking about the particular provision within AISC 360-10 that you're trying to satisfy.
 
Sorry, I was still editing the post. You were very quick to respond lol

I am looking at AISC 360-16 multitier torsional requirement at the beam column connection for braced frame.

Say beam stub will be CJP welded to the column and the stub will be attached to the strut with the connection above. And this connection must have the torsional rigidity per AISC

So was trying to calculate the thickness reqd to meet the rigidity requirement per Appendix 6 torsional bracing requirement
 
No sweat. Are you sure that you don't mean this requirement from 341-16 rather than 360-10? If so, the connection demand is not meant to be torsional but, rather, weak axis flexure. And that probably means flange plates.

C01_mzu9on.jpg
 
Yeah I was talking about this requirement. I correct the typo to AISC 3610-16 above.

So with the web plates, it is nearly impossible to achieve this correct.

Which is used to check the stiffness? Appendix 6 column bracing per AISC 360-10?
 
BAGW said:
So with the web plates, it is nearly impossible to achieve this correct.

I would say so. I can think of one possible mechanism, shown below, but it relies on there not being a gap between the beams.

Are flange plates not viable?

Are beam end plates, with shims if necessary, not viable?

Is there nothing else in the vicinity of the column that could brace it torsinally? A beam on the other side of the frame? A perpendicular beam?

BAGW said:
Which is used to check the stiffness? Appendix 6 column bracing per AISC 360-10?

Appendix six doesn't cover column torsional bracing directly. Instead, they refer you to the article shown below.

C01_dwr0e2.jpg


c02_eza96l.jpg
 
Very informative. Thanks
 