Moment transfer from wall anchor (embedment type) to concrete parapet (RC or min reinforced)

Status
Not open for further replies.

Adam0917

Structural
Oct 3, 2019
6
Hello everyone,

I have a simple question/discussion topic that I want to bring up, share some of my thoughts, and maybe more senior SE can correct me if I'm wrong and provide me with some expert opinions in this regard.

So in my working industry, I have come across many steel wall mount designs that using adhesive/mechanical wall anchors for simple structure that supports telecommunication equipment, e.g. antennas.
Sometimes I have to deal with special requirements, for example, I have a 1.3m parapet (concrete with min. reinforcing I assumed), from the top of the parapet to the proposed antenna is another 1.7m (center of the antenna on which I consider the wind load is acting). In my original design, I left 200mm to concrete parapet edges all around so my anchors can develop full capacity according to the anchor manufacturer's recommendation. Last year, I did not design this type of wall anchor connection to take any moment (i.e. I used pinned connection type).

Recently client has proposed to rise up the antenna so now my total cantilever distance is increased to about 2.1m (from the centerline of the antenna to the top anchor connection). With my re-assessment of the wall anchors, and a closer look at my connection type, I think instead of using the full pinned connection, I tried fixed type, the reason for this is I want to see if the existing connection can take moment at all. Cause I don't have full details of the reinforcement for this parapet, I could only assume none to 15m reinforcing rebars for this parapet, cracked, and 25MPa concrete strength.

So the result was just like what I expected, all the anchors are fine in both tension and shear (far away from their capacities), but I have a problem with the concrete breakout. Now, by just considering the y-axis as my fixed axis, the concrete breakout is at a 169% utilization ratio. I'm now more leaning towards the latter approach cause I know there will be a moment transfer at my top connection. However, I have also seen so many designs by others that had a similar cantilevered structure with wall anchors like this, but they never had a single issue. In addition, My intention is not to touch the existing installation (so this eliminates the option for installing the full penetration rods to engage the entire local parapet wall). So am I overthinking this or my assumptions for parapet were too conservative or am I missing anything?

Loading Case: Fw+Fd, where Fw=1.66kn, Fd=2.88kn (both factored loads). Fw is acting 2.2m above the first connection. overall mount assembly and anchor layout see below screenshot

Therefore, if you are the engineer that deals with this simple design situation, what would you do? Thank you in advance and any advice and input would be greatly appreciated!

Capture-1_ygtcve.jpg

 
Replies continue below

Recommended for you

Couple thoughts

A) If your connection depends on existing conditions then you verify the existing conditions as much as is reasonable. In this case that would mean scanning the parapet to determine existing reinforcing steel. Depending on application coring might be warranted; and in this case, at the top of a building, I'd probably mandate core samples be taken to confirm MPa. You'll be on the hook if the anchors fail because it's 15 MPa rubbish, nevermind the degradation due to environmental wear.

B) You don't talk about resistance of the antenna or its base. Is concrete breakout the weak link or is it the actual antenna itself? If it's the antenna then you have no problem!

C) Based on your configuration I'd figure the joint will be partially fixed (arn't they all!). I might try to estimate the amount of rotation out of the joint, figure the equivalent restraining force, subtract that from the moment you get from the fixed condition (once decomposed to a force couple), and see what results. That might lower your breakout value to a reasonable threshold.

D) If nothing seems to work and you need a fix then simply extend the bolt group until concrete breakout is not the limiting factor. Be careful of group action though as that'll reduce bolt capacity significantly.
 
Thank you Enable.

Just a few of my comments and clarifications to your inputs above:

A): We requested detailed building drawing every single time from our client-side to ensure the wall's structure, but we can only get 1 out of 100 buildings that we do. Not to mention a proper scanning or coring process of that parapet. Such operation first adds extra cost to the client, which they definitely don't want to spend. Plus the landlord of the building doesn't want any coring/sampling etc as well. But I totally agree with you, what if the parapet is made of 15 MPa rubbish concrete and this building has been indeed standing there for at least 20-25 years.

b): It is the concrete breakout at the weak link connection point. Not the antenna itself.

C): I have updated my connection type to partial fixed, that's where I get my moment from, but even based on this, the parapet concrete will fail under breakout.

D): Since the anchor groups have been installed already (last year), and there's not much room all around for me to extend the bolt group any further (sorry the screenshot didn't capture the surrounding objects). Upon our recent site visit, we did not find any cracks or signs of concrete breaking out near the connections. But again, I don't want to risk it by simply rise up the antenna and finish the work. It is also possible that the client would ask for a heavier load to be added at this mount later. So is replacing embedment style anchors group to thru-rods configuration the only option here?
 