Fire Sprinkler Protection for Ceiling Void or Concealed Spaces

Status
Not open for further replies.

engggu

Mechanical
Apr 4, 2021
39
PH
Dear guys,

Do we have any code requirements indicating provision of fire sprinklers at ceiling void or concealed spaces with height of more than 1.2 meters.

Thank you
 
Replies continue below

Recommended for you

Possibly ,,,if qualifies as combustible concealed space


Otherwise,,, not normally
 
What does the sprinkler standard you need to follow tells you? As far as concerns NFPA 13, it does not impose a demarcation line for clearances. It s just a matter of combustibility of the enclosure or combustibility of its contains.
 