Was hoping to get an explanation on why the clear cover (cb) for calculating development length of reinforcement for a beam to column connection is taken at the beam (clear 2 from sketch below) and not at the column (clear 1 from sketch below). In my mind the development location is "inside" the column, so there is no concern of decreased bond strength or splitting due to edge distance. What am I missing?
Clarifications/Example
This is for top/bottom bar cover governing the cb value for the calculation of development length.
#10 top bar
db = 1.27in
fy = 60ksi
fc = 4ksi
cb(clear 2) = 2in
ψt = 1.3
ktr = 0
((clear 1) + ktr)/db = 2.5
((clear 2) + ktr)/db = 1.6
ld(clear 1) = 75in
ld(clear 2) = 47in
37% decrease in material
Clarifications/Example
This is for top/bottom bar cover governing the cb value for the calculation of development length.
#10 top bar
db = 1.27in
fy = 60ksi
fc = 4ksi
cb(clear 2) = 2in
ψt = 1.3
ktr = 0
((clear 1) + ktr)/db = 2.5
((clear 2) + ktr)/db = 1.6
ld(clear 1) = 75in
ld(clear 2) = 47in
37% decrease in material