Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Hilti X-HVB shear connectors

Status
Not open for further replies.

cdowney4

Structural
May 31, 2002
14
Does anyone have experience using Hilti X-HVB shear connectors as an alternative to traditional welded shear studs for composite flexural members? Or have an opinion on their suitability and/or code-compliance in the U.S.?

They seem like a reasonable alternative, with data to justify their shear capacity, but the AISC code seems clear on the definition of a "steel anchor" as a "headed stud or hot rolled channel welded to a steel member..."

The wording of the AISC definition would seem to preclude the Hilti anchors since they are not welded (attached with powder-actuated fasteners) and are not hot-rolled (cold-formed).

I'm not necessarily an engineer that follows the letter of the code when I am confident in my engineering judgement, but am having my doubts on these due to the code language and seeming lack of statements by the AISC or others on their acceptability.

Thanks,
Chris
 
Replies continue below

Recommended for you

I don't have any experience with these or insight into the code path, but I am aware of Vulcraft Ecospan joists, which have a screwed in shear stud. Probably a similar situation as far as code compliance.
 
AISC 360 doesn't preclude using other fasteners. In that case, section A1 applies:

Screenshot_2022-02-23_115747_ecf5zu.jpg


However, most U.S AHJ's require that alternative designs have a current ICC-ES evaluation report. From scanning the website, it doesn't appear that the Hilti connectors have an ICC-ES report yet. They may be able to provide you with some literature or reports that the AHJ will accept.
 