michael333
Hello Out There,
Context:
I'm sizing a natural gas(NG) line (high pressure) from an a tie-in to an existing 6"main gas line over to 4 new gas-fired generators. First time in sizing a high pressure piping section branch.
I'm using the high-pressure gas equation 4-2 from the IFGC. It's been working well for other parts of the system.
I'm deciding between a new 3 inch or 4 inch for this particular piping section branch? My understanding is pay attention to velocity vs pressure drop in sizing high pressure NG piping.
With the above said, here are the parameters:
Have 65 psig available at the beginning tie-in point(node) at the existing 6"main as my starting point for the piping section branch.
402 FT total equivalent length for the piping section branch to the next node,
4": I have a 1.5 psig drop in the piping section branch
3": Have a 5.65 psig drop in the piping section branch,
0.60 SG, 60.0 deg F
My question:
I calculated the gas velocity, based on an equation I googled for gas line sizing. But I'm not sure about my answer due to units in the equation for pipe ID. Inches vs FT.
For the 3" pipe section, I came up with approximately 104 fps vs 250 fps pending if I use inches or FT for the piping diameter in the equation.
Does anyone know which velocity is correct for a 3" Sch 40 steel pipe at the above parameters?
Any advice on which line size to go with: 3" vs 4"?
Thank You,
Michael
Context:
0.60 SG, 60.0 deg F
My question:
Thank You,
Michael