Interesting case study for those here to consider.
Task involved reinforcement of existing PEMB main frame girders. A similar approach could be used on crane rails with hat channels.
Several of the girder's bottom flange lateral braces were removed starting at the haunch and moving in towards the ridge.
Removal of these braces compromised the bending moment capacity of the section and requires retrofit.
Repair strategy involves placing a continuous channel on the bottom flange of the girder over the entire newly unbraced length.
Calculation procedure for this condition was adapted from AISC DG 25 for non-symmetrical sections. Each calculation was run using actual combined section properties, but assuming the section is a plate girder.
Section properties for the combined section are calculated at each end, and the middle of the unbraced length.
LTB strength calculated using Cb and Section 5.4.3 of DG 25.
Findings were:
-Additional Channel increases bending moment strength over the existing condition by around 20%.
-Additional Channel does not preclude LTB, the bending moment strength is still controlled by LTB.
-Not sure what the conventional wisdom on Hat channels for crane rails is, but for this particular section the hat channel does not provide bracing equivalent to continuous bracing.
Hope someone finds this interesting, feel free to chime in with any questions or comments.
Task involved reinforcement of existing PEMB main frame girders. A similar approach could be used on crane rails with hat channels.
Several of the girder's bottom flange lateral braces were removed starting at the haunch and moving in towards the ridge.
Removal of these braces compromised the bending moment capacity of the section and requires retrofit.
Repair strategy involves placing a continuous channel on the bottom flange of the girder over the entire newly unbraced length.
Calculation procedure for this condition was adapted from AISC DG 25 for non-symmetrical sections. Each calculation was run using actual combined section properties, but assuming the section is a plate girder.
Section properties for the combined section are calculated at each end, and the middle of the unbraced length.
LTB strength calculated using Cb and Section 5.4.3 of DG 25.
Findings were:
-Additional Channel increases bending moment strength over the existing condition by around 20%.
-Additional Channel does not preclude LTB, the bending moment strength is still controlled by LTB.
-Not sure what the conventional wisdom on Hat channels for crane rails is, but for this particular section the hat channel does not provide bracing equivalent to continuous bracing.
Hope someone finds this interesting, feel free to chime in with any questions or comments.