Concrete Slab Design for Temporary Transformer 3

Status
Not open for further replies.

Persianger

Civil/Environmental
Jul 10, 2019
3
Hi,

I need to place a cast-in-place concrete slab (8" thick) for a temporary transformer at a job site.

The soil underneath is backfilled with structural material and compacted.

The original design does not show any mesh or rebar for the slab (9'x6'), and the transformer load on the slab is roughly 550 PSF (10,000 lbs total weight of the transformer).

I question whether I need to add a mesh (or rebar) to prevent cracking or for any other structural reasons/requirements.


Thank you!

 
Replies continue below

Recommended for you

...need to add a mesh (or rebar) to prevent cracking or for any other structural reasons/requirements.

Transformer_Footprint-800_oz4381.png
 
Why use many word when picture do trick?

----------------------------------------------------------------------