"I Participated in a FAT (Factory Acceptance Test) for a centrifugal chilled water pump today. The tester relied on the VFD display reading to determine the RPM and kW of the motor during the test. From what I know, use a calibrated torque meter and tachometer for accuracy, and is it mandatory to get the approval from the consultant? I also noticed that the test data clearly indicates that flow will vary when the discharge valve is partially closed at different heads. Additionally, while checking the shutoff head, I observed that the valve isn't completely closed; around 230 GPM still passes through. I brought this up with the tester, and he mentioned that there's no requirement to fully close the valve. thank you in advance for your valuable response