Indoor Vs Outdoor Termination kits 2

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
412
Termination_kit_indoor_outdoor_uiy7pv.jpg


Why the termination kits are applied only for medium voltage and above?
Why skirts are used in outdoor termination kits?
 
Replies continue below

Recommended for you

Skirts are used to increase tracking distance.
Termination kits typically feature either stress cones or an alternate method to reduce voltage gradient stress at the end of the cable insulation.
Before kits were introduced, stress cones were field fabricated by trained "Cable splicers."
Smaller contractors would have to "Sub out" the termination of medium and higher voltage cables.
The introduction of termination kits allowed industrial electricians to complete the cable terminations.

--------------------