Engineers,

Is there any special method to compute settlement on on eccentrically loaded foundations?.

There are many references about considerations for computing bearing capacity but nothing related to settlement.

I have a square footing subjected to lateral force and moments in both X and Y directions. At the same time there is vertical load.

I have seen scenarios in which the moments and lateral loads are ignored and only consider vertical load (P). Then, with that pressure (P/A), if it results in settlement < 1 inch, the recommended bearing capacity is P/A. I am not sure if this is correct. I think at some point lateral loads and moments should play a role.
 
Replies continue below

Recommended for you

Moments change the soil bearing, generally increasing it on one side of the neutral axis and lessening it on the other. Of course that will have the corresponding effect on settlement and also result in rotation. Mc/I is added to P/A to account for eccentricity of loads.

SB = P/A + Mc/I

If there is uplift on one side, the Mc/I will increase the SB on one side by the amount it is reduced on the other. Soil bearing pressures must be recalculated under the part of the mat or footing that does not lift up.

It would be erroneous to ignore any significant increase in SB, rotation and settlement due to eccentricity.

Foundation mats centroid are often adjusted in location such that Dead load Moments are eliminated, in turn eliminating differential settlements between opposite edges.

Temporary live load settlements are often negligible, as wind loads act in one direction on one day and opposite on another, however their increase in soil bearing and potential to cause soil bearing failure as well as overturning must always be checked.

For additional info, you can try searching for "Calculation of soil bearing loads under eccentric loading conditions."