I'm quite shocked to find out that there are no standards that show the formula for generator sizing. Even in our local electrical code. I'm not sure why.
I'm trying to set a standard for our company in sizing genset. Based on several white papers I've read and generator rentals websites, I've come up with this:
Generator kW = (Total running kW of all loads) * Demand Factor - Running kW of largest motor + Starting kW of largest motor
This is loosely based on Siemens Generator Sizing guide except I've included multiplying demand factor.
In estimating the starting kW of motors, is it valid to multiply the motor kW by 600% for direct online connection? Eaton did this in their video (except unit in kVA). However, some articles say that the 600% is for starting current and not kW. I kind of agree since we will multiply the starting current with the starting voltage which is expected to also drop to 70% voltage during starting. In terms of kW, this will result in around 4x the normal kW.
In summary:
1. Is my formula good enough?
2. For direct online, do you agree that the starting kW is 600% or is it 4x the running kW?
I'm trying to set a standard for our company in sizing genset. Based on several white papers I've read and generator rentals websites, I've come up with this:
Generator kW = (Total running kW of all loads) * Demand Factor - Running kW of largest motor + Starting kW of largest motor
This is loosely based on Siemens Generator Sizing guide except I've included multiplying demand factor.
In estimating the starting kW of motors, is it valid to multiply the motor kW by 600% for direct online connection? Eaton did this in their video (except unit in kVA). However, some articles say that the 600% is for starting current and not kW. I kind of agree since we will multiply the starting current with the starting voltage which is expected to also drop to 70% voltage during starting. In terms of kW, this will result in around 4x the normal kW.
In summary:
1. Is my formula good enough?
2. For direct online, do you agree that the starting kW is 600% or is it 4x the running kW?