I'm trying to understand ISA 5.1, Table 4.1 as it might apply to a Gas Detector.
Normally I see a gas detector tags as "ASH..." I've been told that the "S" is for "Safety" and the "H" is for High.
Table 4.1, "A" Column 1 is = Analysis (4-20mA Signal...right?), Blank for Column 2, Alarm for Column 3.
"S", Column 2 is "Safety" and "H", Column 5 is "High"
Does the table mean that the definition for a modifier listed in Column 2 or 5, has to be used as defined under the respective column?
I'm a little surprised I don't see "I", which under column 1 is "Current", and Column 3 as "Indicate". Section 4.2(2) tells me I can't modify the meaning for the 1st letter (Column 1), but I'd be using it in column 3 (output / Active Function) since it outputs a 4-20mA sign.
I'm wanting to assign a tag that allows me to distinguish the different types of Gas Sensors (CH4, CO, H2S, etc)
Since Column 2 is a "Modifier" and for "A" column 2 is Blank, would it make sense to assign a Combustible Gas detector "ACH...) (C for Combustible) or "ATH..." (T for Toxic)?
...also could I use "U" in place of the "H" considering the detector is used to record multiple levels of the gas?