We are designing some new construction projects at hospital which has had poor - if any, CHW closed loop piping treatment for the last 15 years. Long story. On a related note, we have been told that at some time in the past 10 years they hired a local Contractor to "acid flush" the loop piping - their words. To me, this sounds...misguided at best. Our firm had nothing to do with this effort.
For a few projects in the last maybe 5 years, we have installed commercial water filters (36"H x 12" diam), with 20-micron internal socks at AHU's. These seem to protect the coils (no coil blockages since then on units with the filters), but require literally monthly changeout due to iron oxide particles - as fine as flour when crumbled in your hand - clogging the filters. See attached. Note that as of right now, they have NOT had any pinhole leaks in this system.
I have finally convinced then to get a non-destructive ultra-sonic tester, and start measuring some pipe thicknesses at various areas - in particular at junctions that should be at a higher velocity.
Piping is 8" S40 ERW steel, with a wall thickness of 0.322". The question is: How much reduction in pipe thickness is "acceptable" - 10%? 20%? Surely not 25% - before becoming a big problem? The system is about 2000 ft in length, operates at about 50 psi, and to replace it will prove...difficult. Since the CHW Piping was installed in main corridors, they have subsequently installed dozens of electrical conduits parallel to and below the piping, effectively boxing it in. In a great many areas, you cannot even see the piping.
Once the pin hole leaks start, they are essentially doomed to initiate replacing the system. But even a 25% reduction due to corrosion would still leave almost 0.25" of wall thickness.
Any thoughts on how bad is "oh cr@p!" bad?
On a related note, these guys:
have made a pitch to install their system to "clean up" the 8" steel piping. While their photographic before-after results are impressive, I have serious concerns that their system does not "clean up" the system to the point of causing the very problem (pin hole leaks) that we are trying to avoid. I would not want to play any part in having to replace their existing piping due to our "good intentions" to resolve their decades-in-the-making problem.
TIA.
We are designing some new construction projects at hospital which has had poor - if any, CHW closed loop piping treatment for the last 15 years. Long story. On a related note, we have been told that at some time in the past 10 years they hired a local Contractor to "acid flush" the loop piping - their words. To me, this sounds...misguided at best. Our firm had nothing to do with this effort.
For a few projects in the last maybe 5 years, we have installed commercial water filters (36"H x 12" diam), with 20-micron internal socks at AHU's. These seem to protect the coils (no coil blockages since then on units with the filters), but require literally monthly changeout due to iron oxide particles - as fine as flour when crumbled in your hand - clogging the filters. See attached. Note that as of right now, they have NOT had any pinhole leaks in this system.
I have finally convinced then to get a non-destructive ultra-sonic tester, and start measuring some pipe thicknesses at various areas - in particular at junctions that should be at a higher velocity.
Piping is 8" S40 ERW steel, with a wall thickness of 0.322". The question is: How much reduction in pipe thickness is "acceptable" - 10%? 20%? Surely not 25% - before becoming a big problem? The system is about 2000 ft in length, operates at about 50 psi, and to replace it will prove...difficult. Since the CHW Piping was installed in main corridors, they have subsequently installed dozens of electrical conduits parallel to and below the piping, effectively boxing it in. In a great many areas, you cannot even see the piping.
Once the pin hole leaks start, they are essentially doomed to initiate replacing the system. But even a 25% reduction due to corrosion would still leave almost 0.25" of wall thickness.
Any thoughts on how bad is "oh cr@p!" bad?
On a related note, these guys:
have made a pitch to install their system to "clean up" the 8" steel piping. While their photographic before-after results are impressive, I have serious concerns that their system does not "clean up" the system to the point of causing the very problem (pin hole leaks) that we are trying to avoid. I would not want to play any part in having to replace their existing piping due to our "good intentions" to resolve their decades-in-the-making problem.