Aluminum damper in galvanized duct - dissimilar metal corrosion?

Status
Not open for further replies.

m2e

Mechanical
Jun 28, 2006
92
If you put an aluminum control damper (such as Tamco or similar) in a section of galvanized steel duct, would galvanic corrosion be a concern? Similarly, if you have an aluminum intake or exhaust louver connected to galvanized ductwork, would that be a concern too?
 
Replies continue below

Recommended for you

tsqz93do_gv0oam.png
 
Galvanic corrosion depends on direct contact with some electrolyte to carry electrons between them. Merely being in proximity is not enough.

What is the electrical connection between the two metals? What is the electrically conductive liquid? Can the damper be electrically isolated with insulating seal material?
 