"..If you have access to do IR, then you have access to do HiPot. What is the problem here?"
1. Agreed on the accessibility, but...
a) IR can be carried out easily with a say <8kVdc hand crank insulation high resistance meter say about <3kg. Cost of instrument is very low. Most technicians are competent to carry out the test at site
b) DOV test involves much higher Voltage and equipment, especially with AC instead of DC. The total equipments set up may easily be in the range of >100kg !. It needs LV AC power supply, which may not be available at site/in the field.
2. Opinion: In view of the logistic, cost of equipment, competence of the technician, it is NOT recommended to conduct DOV shorter than say 6 months, unless under special reasons. However, IR test on every 6 monthly is NOT excessive.
Che Kuan Yau (Singapore)